10 Oct 2008 18:25 #1 par Anonymous
Re: error
Bonjour,

De façon générale vous devez commencer par regarder la dernière
erreur SEVERE, dans votre cas :
[code]** Severe ** Air Primary Loop 42758 AHU has no air flow
** ~~~ ** Check flow rate inputs for components in this air loop and,
** ~~~ ** if autosized, check ZONE SIZING and SYSTEM SIZING and related inputs.
** Fatal ** Previous condition causes termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=4
..... Last severe error=Air Primary Loop 42758 AHU has no air flow

Le numéro 42758 est un code de zone que vous pouvez retrouver dans le fichier in.idf en cherchant "ZONE, 42758". Ici, la zone 29 du bloc 1.
Enfin le message indique qu'il n'y a pas d'air soufflé dans cette zone (AHU = CTA). En observant votre modèle j'ai effectivement noté que vous aviez choisi une ventilation mécanique 'Par Surface' mais dans l'onglet Activité, il y a 0 l/s-m2 donc pas d'air.

Si vous mettez une valeur >0, les erreurs disparaitront. Attention j'ai aussi remarqué que vous aviez saisie 0 spécifiquement (valeur en rouge) sur certaines zones tout en laissant la ventilation mécanique. Vous devez soit réinitialiser les valeurs en rouge (remise en place de l'héritage depuis le niveau supérieur) soit saisir une valeur > 0 soit ne pas mettre de ventilation mécanique pour éviter d'autres messages d'erreur.

Connexion ou Créer un compte pour participer à la conversation.

Plus d'informations
09 Oct 2008 18:33 #2 par Anonymous
Anonymous a créé le sujet : error
bon jour,
pourquoi mon fichier tombe en erreur?
voici l'erreur:

Program Version,EnergyPlusDLL 2.2.0.025, 09/10/2008 17:52,IDD_Version 2.2.0.025
** Warning ** Requested Time Steps in Hour (2) is less than the suggested minimum of 4.
************* Beginning Zone Sizing Calculations
** Warning ** GetGroundTemps: Some values for "GroundTemperatures" fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** CalcSurfaceCentroid: 76 Surfaces have the Z coordinate < 0.
** ~~~ ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
** ~~~ ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
** ~~~ ** ...that is, these surfaces will have conditions as though at ground level.
** Warning ** DeterminePolygonOverlap: Too many figures [>15000] detected in an overlap calculation. Use Diagnostics,DisplayExtraWarnings; for more details.
** Warning ** DeterminePolygonOverlap: Too many vertices [>15] detected in an overlap calculation. Use Diagnostics,DisplayExtraWarnings; for more details.
** Warning ** Detailed daylighting will not be done for zone=42758
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=42767
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=42777
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=42786
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=42847
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=42973
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43003
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43014
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43025
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43037
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44575
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44602
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44632
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44643
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44654
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44666
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44677
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44686
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43951
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43960
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43970
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=43979
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44040
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44116
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44139
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44166
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44176
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44186
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44196
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44207
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44241
** ~~~ ** because it has no associated exterior windows.
** Warning ** Detailed daylighting will not be done for zone=44250
** ~~~ ** because it has no associated exterior windows.
** Warning ** Calculated design cooling load for zone=42657 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42667 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42680 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42707 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42728 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42749 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42758 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42815 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42825 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42847 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42863 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42923 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42935 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42946 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42955 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42973 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42983 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=42993 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43003 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43014 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43025 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43037 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43048 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43057 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44286 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44296 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44309 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44336 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44357 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44369 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44378 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44387 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44425 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44435 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44444 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44454 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44476 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44520 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44532 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44552 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44564 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44575 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44584 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44602 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44612 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44622 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44632 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44643 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44654 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44666 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44677 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44686 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43850 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43860 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43873 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43900 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43921 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43933 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43942 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=43951 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44008 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44018 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44040 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44056 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44068 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44084 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44096 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44116 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44128 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44139 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44148 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44166 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44176 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44186 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44196 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44207 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44218 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44230 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44241 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated design cooling load for zone=44250 is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
************* Beginning System Sizing Calculations
** Warning ** Calculated cooling design air flow rate for system=42657 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42667 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42680 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42707 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42728 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42740 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42749 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42758 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42796 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42806 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42815 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42825 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42847 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42863 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42875 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42891 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42903 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42923 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42955 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42973 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42983 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=42993 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43003 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43014 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43025 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43037 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43048 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43057 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44286 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44296 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44309 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44336 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44357 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44369 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44378 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44387 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44425 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44435 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44444 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44454 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44476 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44492 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44504 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44520 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44532 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44552 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44564 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44575 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44584 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44602 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44612 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44643 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44654 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44666 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44677 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44686 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43850 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43860 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43873 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43900 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43921 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43933 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43942 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43951 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43989 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=43999 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44008 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44018 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44040 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44056 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44068 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44084 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44096 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44116 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44128 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44139 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44148 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44166 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44176 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44186 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44196 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44207 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44218 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44230 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44241 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Warning ** Calculated cooling design air flow rate for system=44250 AHU is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
** Severe ** InitInteriorConvectionCoeffs: Inside Convection=CeilingDiffuser, but no system inlet node defined, Zone=42913
** ~~~ ** Defaulting inside convection to Detailed. Check CONTROLLED ZONE EQUIP CONFIGURATION for Zone=42913
** Severe ** InitInteriorConvectionCoeffs: Inside Convection=CeilingDiffuser, but no system inlet node defined, Zone=44542
** ~~~ ** Defaulting inside convection to Detailed. Check CONTROLLED ZONE EQUIP CONFIGURATION for Zone=44542
** Severe ** InitInteriorConvectionCoeffs: Inside Convection=CeilingDiffuser, but no system inlet node defined, Zone=44106
** ~~~ ** Defaulting inside convection to Detailed. Check CONTROLLED ZONE EQUIP CONFIGURATION for Zone=44106
** Severe ** Air Primary Loop 42758 AHU has no air flow
** ~~~ ** Check flow rate inputs for components in this air loop and,
** ~~~ ** if autosized, check ZONE SIZING and SYSTEM SIZING and related inputs.
** Fatal ** Previous condition causes termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=4
..... Last severe error=Air Primary Loop 42758 AHU has no air flow
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Severe ** Node Connection Error, Node="42657 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42657 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42667 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42667 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42680 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42680 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42707 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42707 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42728 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42728 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42740 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42740 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42749 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42749 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42758 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42758 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42796 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42796 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42806 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42806 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42815 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42815 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42825 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42825 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42847 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42847 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42863 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42863 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42875 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42875 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42891 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42891 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42903 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42903 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42923 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42923 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42935 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42935 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42946 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42946 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42955 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42955 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42973 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42973 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42983 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42983 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="42993 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=42993 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43003 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43003 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43014 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43014 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43025 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43025 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43037 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43037 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43048 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43048 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43057 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43057 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44286 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44286 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44296 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44296 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44309 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44309 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44336 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44336 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44357 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44357 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44369 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44369 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44378 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44378 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44387 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44387 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44425 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44425 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44435 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44435 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44444 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44444 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44454 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44454 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44476 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44476 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44492 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44492 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44504 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44504 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44520 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44520 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44532 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44532 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44552 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44552 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44564 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44564 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44575 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44575 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44584 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44584 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44602 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44602 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44612 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44612 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44622 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44622 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44632 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44632 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44643 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44643 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44654 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44654 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44666 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44666 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44677 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44677 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44686 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44686 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43850 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43850 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43860 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43860 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43873 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43873 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43900 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43900 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43921 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43921 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43933 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43933 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43942 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43942 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43951 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43951 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43989 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43989 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="43999 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43999 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44008 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44008 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44018 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44018 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44040 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44040 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44056 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44056 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44068 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44068 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44084 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44084 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44096 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44096 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44116 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44116 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44128 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44128 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44139 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44139 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44148 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44148 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44166 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44166 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44176 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44176 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44186 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44186 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44196 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44196 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44207 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44207 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44218 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44218 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44230 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44230 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44241 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44241 AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="44250 AHU SUPPLY FAN OUTLET", Sensor node did not find a matching node of appropriate type (other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=44250 AHU COOLING COIL AIR TEMP MANAGER
** Warning ** DXFOut: Could not triangulate surface="C_42707_1_0_0", type="Roof", check surface vertex order(entry)
** ~~~ ** ...use Diagnostics,DisplayExtraWarnings; to show more details on individual surfaces.